FHW Boiler supply and return size
bill Mc
Member Posts: 1
I have a question about the supply and return piping being too small.
The job has a Utica FHW oil fired boiler with 5 zones one to a baseboard loop three to air hanlder units and one to an inderect fired HW heater which the manufacturer recommends a one inch supply and retun. The current supply/ return is being run in one inch copper.
I say that it is too small and will restrict the flow to the zones if they are all/or just 4 zones are calling on the coldest days.
The job has a Utica FHW oil fired boiler with 5 zones one to a baseboard loop three to air hanlder units and one to an inderect fired HW heater which the manufacturer recommends a one inch supply and retun. The current supply/ return is being run in one inch copper.
I say that it is too small and will restrict the flow to the zones if they are all/or just 4 zones are calling on the coldest days.
0
Comments
-
what is the load?
1" can generally handle 80K @a 20f delta T...1.25 generally 140K....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I do not disagree with Kevin
but would also add that the header flow load in GPM may differ from what your BTU load would otherwise indicate.
My point is, your zone loads may differ in delta-T and therefore flow. AHU coils may take a 30 degree drop, radiation 20 and the indirect whatever it wants.
I would size the header for the sum flow rate of all zone circulators if calling all at once. What is the harm in a header at 1.25" or 1.5" size?
I would suspect the indirect would take the lion's share when calling, so I would make that the first zone, even direct off the outlet of the boiler while the building heating goes straight ahead to the heating zone header. You can see if you keep the 1" common size you will have some fighting in the back seat. (Settle down, kids.)
Bottom line: Size the header for connected flow rate, not BTU's per hour. Be generous such that the pressure drop in the header is minimal.
My $0.02
Brad0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements