I have a Williamson furnace (model# GWA-105N-S). When I got up this morning, my house was quite cold. I went to the basement and the low water (red light) indicator was on.
The furnace starts when the light goes out, but stops as soon as the light comes back on. My HVAC guy is out of town - and of course this would happen on one of the coldest days of the year!
Any quick-fix suggestions?
The furnace starts when the light goes out, but stops as soon as the light comes back on. My HVAC guy is out of town - and of course this would happen on one of the coldest days of the year!
Any quick-fix suggestions?
0
Comments
-
LWCO
Check water pressure, do you hear water in the pipes, your reither getting air by the probe or probe is dirty. but sounds like air boiler runs until circulator starts and pulling air by the probe, purge system of air if thats the case, if no presssure in boiler open valve by waterfeed until it pressurizes.0 -
STeam or hot water?
0 -
Mike
GWA is hot water0 -
In that case
I think Bruce said it all. I'm just wondering if the LWCO is a "Guard Dog" type where they specify a shallow tee where the LWCO is attached. Can't have to much of a horixontal piece where it connects.0 -
Could also be
a Taco LWCO with the "water purity" sensor.
Had trouble with a couple of those so we yanked 'em.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks, Bruce. Your suggestion did the trick. We're snug as the proverbial bugs thanks to you.0 -
Glad it worked
And thanks for letting me know0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements