Is this system piped right?

HAROLDS
HAROLDS Member Posts: 9
Please look at these photo's let me know if some thing is wrong.

Comments

  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Looks right

    Primary/secondary like HTP calls for in the installation manual.

    Why do you ask?


    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jed_2
    Jed_2 Member Posts: 781
    \"PONPC\"?

    > Primary/secondary like HTP calls for in the

    > installation manual.

    >

    > Why do you ask?

    >

    > Mark

    > H

    >

    > _A

    > HREF="http://www.heatinghelp.com/getListed.cfm?id=

    > 238&Step=30"_To Learn More About This

    > Professional, Click Here to Visit Their Ad in

    > "Find A Professional"_/A_



  • Jed_2
    Jed_2 Member Posts: 781
    \"PONPC\"?

    What direction is the primary circ pointed WRT PONC?

    Jed
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    All the drawings.....

    I have show the primary pump on the return, pumping INTO the boiler. Maybe I missed something? Chris.
  • Jim_65
    Jim_65 Member Posts: 184
    Mixing Valves

    Since I don't know what type of system your application is this statement could be false.

    But it looks like a wholesalers dream to have so many thermostatic mixing valves. Why not use variable speed injection with the individual circulators dedicated to specific zones?
  • Nice looking job

    But I agree with the others; the circulator should be on the return as the instructions show in order to properly pressurize the boiler and keep the pressure switch happy.

    Also, the circulators on the secondary piping should have 10 pipe diameters of straight pipe on the suction side, but I see there are space restrictions.

    Other than that, it's a real pretty job.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Seems fine

    The reason most often you see the PONPC on the outlet of the boiler is that it coincides with the air separator. Air is released more easily from hotter water. But with a Spirovent that is almost academic. What you have will remove the air effectively, just may take a few more passes, that's all.

    When the primary circulator is pumping into the boiler (as we agree the diagrams often show) is less of a concern. The head imposed on that circulator is low compared to the distribution circulators and if proper primary/secondary decoupled they ought not affect each other anyway. And as Alan said, the pressure switch issue is satisfied.
  • grindog
    grindog Member Posts: 121
    pump on the return

    That is a nice neat install. The pump should be on the return like munchkin shows in the instructions. You dont want to upset that heat exchanger. That is the first one i have seen piped like that but i am sure it will work.