edr multipler for hot water
clammy
Member Posts: 3,163
could use some help i can't seem to find or rremenber the multipler for edr for hot water rads i know for steam it's 240 but for the life of me i can't seem to find the hot water multipler thanks and good luck and peace clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating
0
Comments
-
For 170 degree average WT
(180 in and 160 out) it is 150 BTUH per SF EDR.
If you want it adjusted for other water temperatures let me know.
Brad0 -
0
-
thanks brad
Thank you brad you are quick man, think i was having a brain fart i just could not remenber ityou the man peace aND GOOD LUCK CLAMMYR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0