sensor
don_182
Member Posts: 69
sensor checked out ok.Found check valve on the recirc loop
stuck open from a piece of solder...this was the reason for not enough hot water.
stuck open from a piece of solder...this was the reason for not enough hot water.
0
Comments
-
Buderus Indirect sensor.
Anyone have a chart that converts ohms to temp for checking
to see if they are working properly? Or maybe a trouble shooting chart.
I seem to have one that is causing problems.
I'm taking a honeywell l6006 with me just in case.
TIA.0 -
Service manual
I'll check right now.
Page 38
http://www.buderus.net/Portals/16/Lit-R2107-SM-01.pdf
Massachusetts
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
i bet,
that if the sensor is changing resistance due to temperature, putting it in ice water/boiling water, it is wroking correct.
really not possible for it to 'go out of calibration'.
isn't this the same question as before, the sensor not being the same as the temp dial? i heard complaints here before that those probe temp dials aren;t that accurate.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements