big boiler small chimney
ANDREW_12
Member Posts: 29
just came from an estimate for a steam boiler, existing boiler 546,000 btu with 12" flue was vented into a 7" clay liner. Of corse the boiler was completely sooted up.
New problem is how can i make this right? Dont think i have any place to run b-vent. Any ideas?
If not a new chimney
how about an Exhausto terminal draft inducer? I do not have the venting tables, but it might be nice to see what they can do with an underside flue.
Get in touch with Steen at Exhausto.0 -
into a clay liner, what about the positve air pressure, is that legal0 -
Negative
The Exhausto goes on the top of the chimney. The chimney is maintained under negative pressure and controlled by a VFD. Very smooth control.0 -
Is the existing boiler
oversized, according to your radiation count?
That is a far better question
and far better answer! Thanks. I will sit back and shut up.
- 87.4K THE MAIN WALL
- 121 Chimneys & Flues
- 15.8K Strictly Steam
