Mr. Gill please
You're one of the many whom has helped me in my education in steam heating. I feel like I'm still missing another piece from the equation. This is what I mean:
Recently on a new boiler install I sold a pressuretrol to vapor-stat replacement. I balanced all 10 rads in the home per your balancing steam systems guide. I set the vaporstat to the equivilant of the lowest setting of a pressuretrol. You guided me to reinstall the vapor-stat at the end of the main.
Before I did that everything heated up evenly on 8 oz. of pressure. Once I reinstalled the vapor-stat at the end of the main & set it to 1 oz. steam pressure, I had a chorus of singing rads & main vents. I felt at the lower pressure, the air vents were now venting too quickly. I installed all gorton #4's & the singing stopped. The system was not as balanced but I got the chorus to stop.
There must be a concept that I'm missing.
What can it be ?
Recently on a new boiler install I sold a pressuretrol to vapor-stat replacement. I balanced all 10 rads in the home per your balancing steam systems guide. I set the vaporstat to the equivilant of the lowest setting of a pressuretrol. You guided me to reinstall the vapor-stat at the end of the main.
Before I did that everything heated up evenly on 8 oz. of pressure. Once I reinstalled the vapor-stat at the end of the main & set it to 1 oz. steam pressure, I had a chorus of singing rads & main vents. I felt at the lower pressure, the air vents were now venting too quickly. I installed all gorton #4's & the singing stopped. The system was not as balanced but I got the chorus to stop.
There must be a concept that I'm missing.
What can it be ?
0
Comments
-
Again as far as the client is concerned the new set-up works a million times better than the old. They love it & have zero complaints. I would just like to make my pencil a little sharper. Thanks.0 -
maybe you should call me
i'm usually around after 7 pm eastern time.. 440-439-4417 so we can better discuss what you have.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements