Balancing a system with out gauges
Adam_25
Member Posts: 1
What is the ideal procedure for balancing a system . From doing a accurate heatloss , one should the ball park flow rates required for any given zone in a system . How would go about getting the ideal flow through each zone . Do you get the ideal flow through the boiler ,which would be additive for all the zones , then set up the seperate zones individually . Would pressure guages be more useful than surface mounted thermostats to set up each zone . Just trying to generate some discusion . Thanks for contributing .
0
Comments
-
I set the primary loop for the boiler requirements, then set the secondary zones by heat requirements. I balance by using lower speeds and check the rads on the zones one by one, until I know the heat is even and the ret heats reasonably. TV keeps the ret temp happy, and ODR keeps the supply temp where it needs to be.
TimJust a guy running some pipes.0 -
Guages and Thermometers
I use both. The balancing valves I use have T&P (temperature and pressure) ports built-in. These are also known as "Pete's Plugs" and allow a needle guage fitting and a probe type thermometer to be inserted into the water stream.
I use a Dwyer digital pressure guage and the balancing valve circular sliderule to determine flow based on delta-P and valve setting (absent an in-line flow meter).
For temperature, this can corroborate your flow reading and other things but takes more time. The reason is that most systems are rarely steady-state. When up-firing, the delta T will start wide then narrow. DHW does this to illustrate. A good system will respond to the dynamics hence the variables are always changing. Once warmed up though, you can get a relative snapshot of how your system is performing.
I agree with Tim, set up the boiler separately from the emitter circuits.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements