combustion air
Does anyone know if 6" round galv. piped from outdoors will provide enough combustion air for 140,000 btu?0 -
very helpful, thank you very much.0 -
Not really
By square inches you would need at least 35 which would be a 7" pipe. The mistake that is often made is that this pipe is only supplying combustion air to the boiler. That pipe will supply air for the total ventilation of the building if it is not in an isolated mechanical room or the flue pipe will supply the rest. Passive combustion air has no better than a 50% chance of working. Need fan powered mechanical air to guarantee real combustion air.0 -
I agree with Jim.
A Tjernlund or Exhausto pressure-responsive combustion air system is a nice way to go. Works via a VFD to maintain a positive pressure in the boiler room or enclosure.
An expense but worth it especially if it helps save your life.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements