Another main vent question
Options
Dave Miller
Member Posts: 26
so I'm posting this diagram with the question; should I worry about drilling and tapping for venting the branch/sub branch? It looks like a good spot would be just before the return drop, next to the main vent (see photo). I have a Gorton #2 on order to replace the Hoffman #4 on the main. Most of the rads are only partially heating up. Of course, it's been pretty warm here in the Fingerlakes country....
Thanks,
Dave Miller
Thanks,
Dave Miller
0
Comments
-
The proper place for that vent
would be at the end of the 14-foot sub-branch, near the takeoff to the last radiator. If the Hoffman you're removing from the long main is a #4A, it would work OK on the sub-branch.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0