Buderus settings
Big Ed_3
Member Posts: 170
In the service manual , listed in the first few pages there will be changes to the setting you need to do . Best off leaving the off set to 0 for now. The reference temperature depends on the amount of radiation installed in the home. You will need to set it for largest load or the the zone with the least amount of radiation per heat loss . Try first to leave it at the factory setting of 167*. If you need a few more degree in living space on one of the zones bring it up a notch, try 170*.
logamatic settings
I have a 3 zone system. the main zone has a bfu room sensor. What is a good recommended ref. temp, Offset, Etc...
- 87.4K THE MAIN WALL
- 121 Chimneys & Flues
- 15.8K Strictly Steam