propane fired peerless pinicle

Chris_84
Chris_84 Member Posts: 7
The intake and exhaust are a good 8 feet from the corner of the house. and the original install on the first unit was another 3 feet further. I'm not able to supply pic's at this time.

Comments

  • Chris_84
    Chris_84 Member Posts: 7
    propane fired peerless pinicle

    I'm on my second brand new peerless pinicle boiler. The new boiler like my first one is constantly locking out (fo9 code). Also when the boiler is between running cycles, warm air (w/condensation) and some gas smell blows back out the intake of the blower right onto the main electrical board. The boiler is said to be installed properly,intake and exhaust and electrical.
    The first boiler produced the same problems and after a year of not finding the problem and changing parts (flame rod,main electric board and blower) the unit still locks out. The factory rep finally agreed to a new boiler and the new unit locks out. HELP
  • GW
    GW Member Posts: 4,831
    basics

    were the gas pressures set? all the joints glues? condensate draining freely? Polarity correct? incoming gas pressure good? correct orifice?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Chris_84
    Chris_84 Member Posts: 7


    yes to all but one. unsure of the proper gas pressure. at one point it was checked ,but I din't think it was check while on a long running period. I plan on calling the gas supplier and asking them to check the regulator. the lock out problem seems to occur more when it is colder out than normal.
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395

    There was an error rendering this rich post.

  • Cosmo_3
    Cosmo_3 Member Posts: 845
    I'll second that

    How long is the venting? Remember to account for 90's when calculating the total linear feet.

    I went to trouble shoot a Munchie installed by different contractor, and the problem was the pvc venting was too long.

    Also check for obstructions, in the piping and the terminal.

    Gas pressures important also.


    Cosmo
  • Chris_84
    Chris_84 Member Posts: 7


    The intake isn't blocked and the exhaust is pitched properly back to the unit. The condensate is draining properly.And it's well within the number of feet fo the run.
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395
    Again..

    Check the venting. Not the length.

    Try checking the relationship of the intake with the exhaust.

    Are they located in or near a corner? (either inside or outside corner)

    Can you post pics?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • Cosmo_3
    Cosmo_3 Member Posts: 845
    Thanks Al

    Forgot that one, was it Jamie that happened to?


    Cosmo
  • Chris_84
    Chris_84 Member Posts: 7
    vent

    when this second install was done the placement of the vent was by the manual for the distances.
  • Chris_84
    Chris_84 Member Posts: 7


    Thanks for the ideas. Iv'e got to get back to work.I'll see what the gas supplier has to say tommorrow.
  • GW
    GW Member Posts: 4,831
    yeah

    I've heard of regulators going bad; fussy in cold/freezing weather.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Dick Charland
    Dick Charland Member Posts: 178


    Was this installation set up with combustion test equipment?