3/4 Kitec feeding 2nd floor panelrads
Solarstar
Member Posts: 82
wall is apart and I need to feed the second floor for future panelrads. Will the 3/4 kitec carry about the 20K btus Max required for this. I think kitec pipe is a full 3/4 I.D. thanks Paul
0
Comments
-
3/4\" will ...
work but so will 5/8" (id that is)...1/2 would work if you had only 15k...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
1/2\"
will move 20,000 at a 20 degree delta t (2 gpm) 2.6 fps with 5.5 feet of head per 100 feet of tube.
5/8" would provide a little breathing room.
hot rod