I am having a problem with a Victroy VF-1 single door freezer. The drain freezes up. Anyone experiance this problem before?
Thanks
Don in MO
I am having a problem with a Victroy VF-1 single door freezer. The drain freezes up. Anyone experiance this problem before?
Thanks
Don in MO
0
Comments
-
V is for Victory!
Hi Don !Possibly debris in drain pan blocking the drain hole, or a plugged drain line or a plugged drain trap(if there is one) or a drain line heater or drain pan heater not physicaly close enough to drain hole ! Does this help?0 -
yep
Many of them need to add a heater inside the drain line. Forgot if we got them right from victory or were using bev air ones.0 -
Try hanging
a copper wire around the defrost hanger and let about 3" of into the defrost drain.0 -
SAM
What a cool idea !0 -
Victory no help
Yes I will be getting a drain tube heater or the copper wire. Talked to Victory today and they wanted to know how cold it was. I told them 0, since it is a freezer and had already been told that it would freeze the drain line if it was below 0. Now how do you explain to a customer that your freezer is too cold?!
Anyway the suggestion was insulate the drain line or get a heater for it, but not from us because it doesn't need one.
Thanks for the replies and will find out in about 4 months or so how it works out.
Don in Mo0 -
Don
Happy T-Bird day to you and yours! Why the waiting time to find out?0 -
heat it
Get the heater.. what happens is a very very very small amount of water is left in the bottom of the drain tube at the end of a defrost and freezes between defrost cycles. The frequency depends on if the plastic drain line has been even looked at it seems. After seeing 3 of them started looking real close at ones people were not complaining about sure enough the drains were partially frozen some more than others.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements