WM Ultra Troubleshooting
Steverino
Member Posts: 140
Here's the link: http://forums.invision.net/Thread.cfm?CFID=2440484&CFTOKEN=1f084cc-dc52b25a-5c67-446c-aa4d-cf08949c6603&CFApp=2&Thread_ID=41819&mc=11
0
Comments
-
WM Ultra Troubleshooting
I have a WM Ultra 155 with an outdoor reset. The heater stopped working. After checking a few things, I realized my outdoor reset was registering the outside temp at 230 degrees. No wonder the heater wasn't turning on. Is this a problem internally with the control board or a problem with the outdoor reset thermometer?0 -
Its the outdoor sensor....
If the sensor shorts it will read 230, if it is open it will read -22... for now just unhook one of the wires going to the sensor so that it reads the -22 and you will at least get heat... you can back down the max. setpoint temp. if you don't need to have the boiler running that high of temps. right now.
I don't think that your boiler is that old...WM will probably replace the sensor under warr. for you.
Make sure the one they replace it with is the round one, not the little oblong one. The round one's are better....
Floyd0 -
Once again, thanks
Floyd, You have been a big help these last two years. Thanks. Heating Help has become a place for all to come for information. Your advocacy for heating professionals is refreshing. Thanks again.... Triplet Dad0 -
I just found this on two local Ultras, and Josh posted to indicate that he too had some issues with the outdoor sensors, and that sealing them up with silicon stopped the problems. Apparently it was water or spiders or something getting in there and messing with the sensor.0 -
Ditto
My Ultra appreciation goes out to Floyd as well, for ultra amount of information he provided with my setup.
Floyd and many others on this site truly are the definition of ULTRA-uism at it's very best, Kudo's for your help>>RichC
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements