estimating cubic feet of air in pipes
Options
Uni R_2
Member Posts: 589
You can put this in a spreadsheet.
Let's say cell B2 is the diameter in inches and B3 is the length in feet.
In B4 the formula to calculate the CF would be:
=((B2/2)*(B2/2))*3.14159*B3/144
Or as a quick and dirty Dia" x Dia" x Len' x .006
3" x 3" x 25' x .006 = 1.35cf
Let's say cell B2 is the diameter in inches and B3 is the length in feet.
In B4 the formula to calculate the CF would be:
=((B2/2)*(B2/2))*3.14159*B3/144
Or as a quick and dirty Dia" x Dia" x Len' x .006
3" x 3" x 25' x .006 = 1.35cf
0
Comments
-
cubic feet of air in pipes?
Hi everyone. I'm the new super of a steam heated 157 unit building in Manhattan. Due to what I'm assuming was either ineptitude or lack of concern by former supers, I have a big heating mess on my hands. Thanks to Ken at Gorton's, I was directed to this site. My previous building did not have steam heat so I'm desperately trying to figure out this system before the Arctic blasts arrive. I've ordered a couple of the books (which have yet to arrive)and "Balancing Steam Systems" (the e-book... which has been incredibly helpful so far).
Anyway, my question: (and I'm sure the answer is so obvious it hurts) how do you figure out the cubic feet of air in the pipe that needs to be vented? I know it has to do with the size and length of the pipe (My mains are 3"). If I look at system drawing #1 from "Balancing Steam Systems" I see that 20 ft of 1 & 1/2 pipe = .28 but I don't know how one arrives at that. I'm sure there is a standard on the cf in any size pipe, but I don't know what it is.
I would appreciate any help I can get on this. Thanks!0 -
thanks
Hey Uni R,
Thanks so much for the information. I truly appreciate the help.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements