vent connector question
Options
Timco
Member Posts: 3,040
Two WH, 40kBTU each, and 162k boiler. Tables I looked at say sizing is good, but which section deals with the order in which they connect? And which section deals with double / vs. single wall? Old WH connector was split right down the top, and sagged everywhere. I will strip the tape tomorrow. Old WH connection was stuck next to the old boiler connection through some knocked out bricks...unbelieveable. Suggestions for venting changes?
Just a guy running some pipes.
0
Comments
-
manifold
In the 2006 fuel gas code the picture is on page 160 figure G.1(k) 13.2.4 on page 115 is the detail. You have a 10% common vent reduction at the manifold and the length can't exceed 18 in/in of common vent connector diameter. The upslope is the std 1/4 in/foot and the support is the same as any other vent connector. Using b vent for the manifold is an excellent way to max vent effect.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements