Best way to equalize stream radiators?
Options
Vito Cavallo
Member Posts: 23
I have a small house with a one pipe steam system. House is 2 floors not including basement, 4 rooms per floor.
I have just had my old 50's oil burner replaced with a brand new Smith oil burner. I insulated the mains and replaced all of the vents on my radiators.
Question is, what is the best way to start adjusting my radiators? How wide do I open the first floor vents assuming they are the closest, and how wide do I open the second floor vents assuming they are the furthest from the boiler?
I know I will need to tweak because my radiators are different higths and lengths, but what is a good rule for the initial adjustments? Right now, all vents are wide open and the second floor bedroom is 8 degrees hotter than the first floor.
Thank you
I have just had my old 50's oil burner replaced with a brand new Smith oil burner. I insulated the mains and replaced all of the vents on my radiators.
Question is, what is the best way to start adjusting my radiators? How wide do I open the first floor vents assuming they are the closest, and how wide do I open the second floor vents assuming they are the furthest from the boiler?
I know I will need to tweak because my radiators are different higths and lengths, but what is a good rule for the initial adjustments? Right now, all vents are wide open and the second floor bedroom is 8 degrees hotter than the first floor.
Thank you
0
Comments
-
venting
Have you vented the main well? What's the time from the beginning of one heating call to the next?0 -
Start with them all open wide, for fast venting.
Each day that the heat is used (leave the thermostat set in one place), adjust closed a LITTLE BIT, the vent in the warmest room.
Each adjustment affects ALL of the radiators, in some small way. Don't adjust too much at once.
Noel0
This discussion has been closed.
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 113 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements