Backflow preventer and prv's
Options
mtfallsmikey
Member Posts: 765
Especially if you have to use an RPZ type backflow preventor. Flush the line first tho.
0
Comments
-
thinking out loud
Would a viable solution to backflow preventor discharges be to pipe them after the prv to be on the low pressure side?0 -
No...clean the check or allow the water in the fill line to acclimate. Check wants full house pressure, then PRV.
TimJust a guy running some pipes.0 -
prv bfpi
We have had to change quite a few that people have put on the outlet side of the prv, no pressure differential for the bfpi to see so it opens up. Also make sure to put a Y strainer before the bfpi, this will save some service calls.0 -
Water hammer
Water hammer can cause a small discharge from the backflow especially an RPZ.
We install a simple spring loaded 1/2 check before the backflow.
That stops the small discharge from water hammer.
Dave in NH0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements