Fields SWG-III power venter
Bill Nye_2
Member Posts: 538
combustion air, make sure you have make up air. If the house goes negative while the burner/power vent is cycling then on the off cycle cold air will enter the house through the power venter. This could cause condensation too.
0
Comments
-
Ive been seeing lots of power vented oil FHA furnaces vented with the Fields SWG-3 power venters .
Alot of them have serious condensation issues in the flue pipe, judging by the white powderlike build-up at the pipe joints.
Any solutions?
Thanks Tom
0 -
Post purge
Make sure you have enough post purge timing. Make sure you are only pulling .03 - .04 draft in the breech. Make sure the burner is not underfired by too much.0 -
Thanks Bill, the house I was at tonight does have a comb. air problem. The dead giveaway was when the cellar door slammed shut after the blower ran for about 10 seconds.
I left the cellar window open for the night. Told cust. we had to do some changes to duct system.
I have to back tomm. to check a couple other things, I'll check out the post purge.What would say is a good PP cycle time? 3-5 min.0 -
Fan in a can
I have been using Fields fan in a can lately with good success. 3-5 is good. I see a lot of them set to shut off ASAP. Guess they don't wanna waste heat.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements