with only a supply line from the tank. You will need to look at the instructions for the tigerloop as well as the pump to determine pipe sizing as well as whether or not a lift pump (no tigerloop needed) or two stage pump needs to be used. Use the bottom of the tank as the oil level because that is the worst case. Hope this helps.
Tom M.
Tom M.
0
Comments
-
Tiger loop
Can anyone tell me about a Tiger loop on an oil line? It's going to be on a line off of an indoor,above ground oil tank line. It supplies a duct furnace about ten feet off the floor on a mezzanine level. he piping run is about 35' for the supply and 35' for the return. Any info would be greatly appreciated.
Anthony Menafro0 -
Tigerloop
If you are using a tigerloop, then why are you running a return line? A tigerloop, is installed near the burner, and connects to the burner using a supply and return line. But you only need a supply line from the tank to the tigerloop. This is clearly explained in the tigerloop instructions.
Why are you using one?
Always check the oil pump install manual to check to see if it can handle the lift, and run of oil line from the oil tank to the burner. What burner is installed in the furnace?
Cosmo Valavanis
Dependable P.H.C. Inc.0 -
For years, Tigerloop has been primarily thought of as a problem solver, a "band-aid," used to economically cure air and suction line problems. But, that's only part of the story! All systems benefit from Tigerloop's unique ability to condition the oil prior to burning. Whether it's air elimination, nozzle coking problems, vacuum reduction, oil preheating, or just the elimination of that potentially leaky return line , Tigerloop is today's safe, economical choice for all oil supply systems.
The Advantages of Tigerloop...
Safely Handles suction line air leaks
Reduces running vacuum for clear, foam-free oil at the nozzle
Removes air entrained in oil during transporting and delivery
Eliminates potential leak hazard by eliminating the return line
Preheats oil for cleaner combustion
Extends filter element life
The ever-popular Tigerloop removes residual air from the fuel, promoting enhanced boiler efficiency, cleaner combustion and a more efficient burn. The Tigerloop also does away with the need for an undesirable return line on top outlet and wall mounted installations.Tigerloop offers more reliable and environmentally-friendly oil installations. Tigerloop does not only de-aerate the oil. Because only one pipe is used between tank and burner, the installation is cheaper and safer because a return pipe is not needed and the risk of oil leakage is therefore significantly reduced. The one-pipe system, as it is called, also means that considerably cleaner oil is drawn from the tank.
0 -
One pipe
Cosmo, After reading about the Tiger loop, I see that you and the others who responded to my thread are correct in that only one line is necessary. After I posted my question, I was able to find some info through this site. I also agree that the loop is beneficial to the systems performance in all aspects. Thanks to all who responded. I will contact my local oil parts supplier tomorrow(oops, I mean today) and pick up a Tiger loop and make sure of the other questions that you guys posed to me.
Anthony Menafro0 -
the reason
I asked why you want to install a tiger loop because maybe you have an unrelated problem taht the Tigerloop may not address.
I use Tigerloops on basically every new oil burner install. In addition to all the benefits listed by the other posters, one major benefit is the fact that the oil line will only pull what is needed by the nozzle, as compared to a 2 pipe system. Filter life is increased tremendously, and in cases where you are pulling oil from an underground tank or from outside an additional benefit is that by eliminating the return line you eliminate the condensation that occurs when a two pipe system pulls oil in the building, then after warming the oil spits it back in the tank.
The only place I may refrain from using a tigerloop is on situations where the oil tank is signifigantly higher than the burner. But refer to instructions and you will be fine.
Cosmo Valavanis
Dependable P.H.C. Inc.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements