wierd problem burnham IND8
clammy
Member Posts: 3,162
I believe steamhead has hit the nailo on the head i believe it's a hydrolevel lwco electronic .Installed a peerless that came equipted with it did not like the fact that it cycles the burner on self test .On the system i did the t stat cycles the boiler not yet has it cycled on the pressurtol because of this stupid self test the boiler ends up with a lag in producition of steam giving me slight distrubtion promblems with end of the run rads on second floor and over heating on the rads near the boiler closer to the stat .At least that's my thoughts but this job also has the issue of very old original traps that are in need of replacement and my buddy didn't mention this to the HO which was the first thing i said besides replacing a clogged and leaking semi buried wet return and the HO i believe thinks that should have been included in the price and really doesn't want to pay more but was informed of possible replacement of .Is it me or is it everybody with steam traps on there rads all mostly always refuse to do maintance or replace unless there frezzing peace clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating
0
Comments
-
wierd problem burnham IND8 gas boiler
I looked at a burnham IND 8 section boiler on monday its a steam system after it runs for 20 minutes or so it shuts down for about 2 seconds then turns on again i cleaned the pigtail of gunk and ran the boiler and it still did it put my meter on the terminals on the pressuretrol and to gound never lost 24 volts at pressuretrol was wondering if anyone else has any ideas vthis boiler has been diong this for 3 yrs
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Hey Ed,
how you been? What about the lwco, loose wire on probe maybe. John0 -
Or
is it one of those LWCO units that shuts down every so often by design? Hydrolevel maybe?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
wierd problem
boiler is wired 34 volts to draft damper then into lwco then into pressuretrol then back to 24 volt ground on ignition module i will pull and clean then lwco and srr if that helps
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements