Should steam return lines be insulated?

Al Cobrin
Al Cobrin Member Posts: 8
I was advised when I asked (here) a few weeks ago about whether return lines in a steam system should be insulated, that it's good practice to insulate all lines. So I did just that and insulated all of my return lines with preformed sections of fiberglass insulation.

Now I've read somewhere that "the return pipes should be uninsulated to promote condensation."

My question is: did I do wrong?

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Insulate

    The returns are filled with water. The cooler the water gets, the more it will absorb carbon dioxide, which creates carbonic acid, which eats the returns.

    Henry's Law.
    Retired and loving it.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Thanks for the reminder, Dan.....NM

  • Gene_3
    Gene_3 Member Posts: 289
    Ohhhh

    Henry
  • JoeV
    JoeV Member Posts: 62
    My dead men...

    ...Must not have paid attention in chemistry class. They stopped insulating right after the last radiator in each main.
  • Al Cobrin
    Al Cobrin Member Posts: 8


    I SEEM to be getting conflicting advice concerning insulating steam return lines. I take it you are saying that they should be insulated to reduce pipe deterioration. That's fine, though my rationale is to reduce gas consumption. Others seem to say that they shouldn't be insulated, and that I should've paid closer attention in chemistry class. Could you be more explicit, please?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    The hotter the return water,

    the less it needs to be heated by the boiler. That saves fuel. The hotter condensate is also less likely to damage the pipes by corrosion.
    Retired and loving it.
  • Caselli
    Caselli Member Posts: 40
    return pump ?

    They may be thinking there can be an issue if there is a condensate return pump -- re the promotion of condensation.

    More so prevention of flashing back into steam on the pump suction side ?
  • soot_seeker_2
    soot_seeker_2 Member Posts: 228
    Back then

    Fuel oil was 2 cents a gallon when they decited not to insulate those returns.

    Now they should be insulated. It can only save money and will slow down the rotting of the returns.