Taco SR503
Mike Reavis_2
Member Posts: 307
through the panel> You would take the common from the power supply to the zone valve motor, hot to and through the thermostat, and back to the zone valve motor. End switch of the zone valve to the t-t of the panel. Do not however use the old style heat-motor Taco zone valves with this application.
0
Comments
-
Taco SR503
Is it possible to use 2 zone valves along with 2 circ. pumps with this control if so I need your input...Thank You Shawn0 -
Taco
So from zone 1 hit the valve then t-stat and back to the other side of zone 1 same for zone 2? T-T sends signal to boiler to fire0 -
No, I don't think so.
> So from zone 1 hit the valve then t-stat and back
> to the other side of zone 1 same for zone 2? T-T
> sends signal to boiler to fire
0 -
No, I don't think so.
You need to get 24 volt power from the panel, or from another transformer. If I remember correctly, the 24 volt power is toward the top, on the left side of the panel. Common to the zone valve uninterrupted, hot, to and through the t-stat to the zone valve. The end switch of the z-v will be used to close the connections on the panel for the circulator. Your boiler is energized through the x and x terminals.
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements