overfill
Options
[Deleted User]
Posts: 55
residential steamer w/ hw coil...double header.. customer called and said that water was too high in the gauge glass.. went there and drained the boiler down to a good level..let it cycle and nothing.. customer calls back 2 days later and says he drained the boiler down and the feeder cam on and stopped when the cutoff was satisfied.. 3 hours later the water level was high again.. feeder malfunction or cutoff malfunction? mm unimatch feeder and mm 802 w/ manual reset
0
Comments
-
isolation
Before you blame the uni feeder isolate the water feeder and have the ho check the water level if it doesn't rise then it's not the feeder if it does then you probalby have a small leak on the tankless coil isolate it to be sure and if the level does not flood then there's your culprit ,i have seen this a few times on steamer it's sometimes overlooked it can be a bit easier on a hot water boiler it blows the saftey but the procuder is the same peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements