main vent size
Steamhead (in transit)
Member Posts: 6,688
We'd recommend 2 Gorton #2s on the longest main, a Gorton #2 and a Gorton #1 on the next shorter main, and a single Gorton #2 on the shortest main.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Main vent big enough?
I've got vent rite #35s on the following mains:
- 100' 3" main
- 75' 3" main
- 45' 2" main
Does somebody know if the vents that I have are sufficient for normal performace of the system?
Thanks,
D
0 -
If it helps, the steam boiler that feeds the mains generates 1200 sq ft of steam.
Thanks,
D0 -
I think we need more
three on the long one, two on the middle one, one on the short one. All Gorton #2 vents.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
By the way, would you guys happen to know how much EDR these mains would add to my 1100 sq ft EDR from my radiators? I used a pickup factor of 1.5 when sizing my new boiler. Is another 550 EDR all I should need to add to my total EDR calculation for these mains?
Thanks,
Diar0 -
That
should be plenty. It may even be a bit too much, since a 1.33 pickup factor is already figured into the boiler's Net rating.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks. To be certain, the boiler has a 1650 sq ft steam gross rating, my radiators account for 1100 of this and I was hoping that the 550 left would be enough to account for the piping.
Still sound good enough?
- Diar0 -
You'll probably end up
down-firing that boiler slightly.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements