tomorrow I fire it...opinions?

stormin
stormin Member Posts: 4
Are theses thermic bypass valves always included in boilers systems manifolds or just when using condensing cast iron boilers?
Hi, I am designing a 5 zone system w/3zone infloor, fan watercoil, indirect DHW, on a new buderus 125kbtu boiler
Am gettin conflicting advice on whether to use mixing valves to each infloor zone, whether to use individual circs or 1 circ and zone valves and just how to prioritize the DHW. Any input to shed more lite on the subject? Plus it all needs to come together on the wall like a work of art(demanding client even painted the wall for mounting all the manifold systems)
BTW, I used Onyx tubing & it's so easy to work w/ when laying down radiant floor tubes. I see most everyone using pex which seems abit stiff. Just My 2 cents worth.
STormin

Comments

  • Timco
    Timco Member Posts: 3,040


    Just have the returns and the gas to finish, and the controls. I should be able to fire it tomorrow. Any suggestions?

    Tim
    Just a guy running some pipes.
  • Ray M
    Ray M Member Posts: 94


    I would install a low water cut off on the supply riser before the union.

    Thanks
    Ray M
  • Timco
    Timco Member Posts: 3,040


    Is a LWCO typical even with a auto-fill system that is left on?

    Tim
    Just a guy running some pipes.
  • Ray M
    Ray M Member Posts: 94
    LWCO

    > Is a LWCO typical even with a auto-fill system

    > that is left on?

    >

    > Tim



  • Ray M
    Ray M Member Posts: 94


    The LWCO in westchester county n.y. is code. You wont pass with out it.

    Thanks
    Ray M
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    A LWCO anywhere in NY state


    is code and it's just a good idea.

    Nice work Timco.

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • rucomfy
    rucomfy Member Posts: 43
    Just wondering...

    > Just have the returns and the gas to finish, and

    > the controls. I should be able to fire it

    > tomorrow. Any suggestions?

    >

    > Tim



    Looks real nice. Besides the LWCO (I believe it was mandatory per code 2003), why all the foil tape on the single wall vent connector? Are you sure single wall connectors are allowed by the Vent Tables ? How about the appliance with the lowest input being first into a common manifold ? Other than some vent questions, looks nice.
    I like that Xtank mounting.

    Just noticed the tee on the water heater what else is on that manifold. I think we need to recheck the Vent Tables.
    What do you think?
  • Ted_9
    Ted_9 Member Posts: 1,718
    nice

    Looks nice and neat. Well thought out. Quality parts too. And I like the expansion tank install.

    What's with the silver tap? Is it rated for high temp?

    And what is the item on the bottom of the primary loop which ties in to the bottom tee? I'm interested.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Cosmo_3
    Cosmo_3 Member Posts: 845
    Ted

    That is a Danfoss ESBE Thermic bypass valve. As installed it will bypass the system, and return all water back to the boiler until the return temp hits 140. It will respond to cold water return temps from the system by adding hot water from the supply header. I really like them, they are simple and only ever had one callback one one. It uses what looks like a standard automotive coolant thermostat, (well I'm talking Ford/Chevy/Dodge anyway)

    I have the same questions as above on the LWC, the tape, and the Exhaust manifold. I also think the taco circ on the primary needs to be rotated so the wiring box is on the side instead of the bottom where it may be damaged by water leaks per manufacturer.

    Looks like you spent a lot of time on it, looks very neat and proffesional. I like the expansion tank mount, that is not going anywhere soon, and easily accesible for service. I also like the drain port under the air eliminator.

    We all look at our installs after we are done and see where we can make improvements.....


    Cosmo
  • Timco
    Timco Member Posts: 3,040


    That is a TV valve. See the post 'ever use a TV?' My helper ran out of screws...and taped it. Needed to get them hot water. I am hoping the tape will come off after it gets hot. Could you point me to the code that concerns the smallest appliance being first? If it needs to be changed, I will. I have had many inspections now and never been asked about a LWCO. Just 30# relief & backflow & vent size. The rest is totally greek to our inspectors here.

    Thanks for the words...I really try, you know!

    Tim
    Just a guy running some pipes.
  • Timco
    Timco Member Posts: 3,040


    I posted a second ago...Which code deals wit the order of introduction into the manifold? I will bring in my IFGC book. Only two WH's and the boiler. Foil tape comes off. It was temp because helper ran out of screws. It got the cust hot water....

    T
    Just a guy running some pipes.
  • Cosmo_3
    Cosmo_3 Member Posts: 845
    Don't apologize

    You have no reason to feel bad, your work is top shelf. You asked for suggestions and we gave them. I could show you some of my jobs that were done ASAP, and when time permitted went back and corrected.

    The tape is a good idea in lieu of screws, I would have done the same thing.

    You are a brother wethead.... we are FAMILY!! (think Pointer Sisters)

    Cosmo
  • Near boiler piping...

    is that Glavanized steel pipe on the near boiler piping?

    After seeing what happens in open potable DHW systems with galvy pipe, I never considered it much good for anything but fence posts :-)

    Nice clean install.

    ME
  • Near boiler piping...

    is that Galvanized steel pipe on the near boiler piping?

    After seeing what happens in open potable DHW systems with galvy pipe, I never considered it much good for anything but fence posts :-)

    Nice clean install.

    ME
  • brucewo1b
    brucewo1b Member Posts: 638
    Mark that too was my first thought

    but after zooming in on the pic it looks like Black, I agree on the galvy and good install Tim
  • rucomfy
    rucomfy Member Posts: 43
    National Fuel Gas Code..

    Section 7.10.4 paragraph C Vent Tables Section 11.
    Gotta go.. keep up the good work
    BTW combustion air provisions 50 cubic feet per 1000 input?? for unconfined space definition..
  • Timco
    Timco Member Posts: 3,040


    I am good on combustion air & and makeup air, but cannot find the code section you refrenced.Ihave Chimneys & vents as section 501, chapter 5. tables are 504. Any ideas why the two IFGC would be so different? I would like to read this & learn!

    Thanks again,

    Tim
    Just a guy running some pipes.
  • John Mills_5
    John Mills_5 Member Posts: 952
    I'm learning

    what is that piping method? Is that primary-secondary? If so, why the bypass valve? Is this a converted gravity?
  • RianS
    RianS Member Posts: 104
    Nice work Tim

    While you are finishing the fuel line for the boiler maybe you could repair the fuel line on the water heater. Customer would probably like to get rid of that flex connector.
  • Uni R_2
    Uni R_2 Member Posts: 589
    Yes it's P/S

    And a nice example too. The thermic bypass is to allow the boiler to warm up, much the same way your car does. It recirculates the water inside the boiler until it is warm enough and then lets it through for the heating circuit. The boiler runs better and cleaner this way.