Low Water Cutoff - Probe Primary - Float Secondary
Dale
Member Posts: 1,317
Without seeing the specific install instructions I'll just give an informed opinion. On all the steam boiler install instructions I have seen the tap for the probe type is above the float type water shut off line. This is done to give a little more time for condensate to come back. So, if the first one is higher in the water level I guess it would be first to shut off. Also, in some states the lwco must break the 120 volt feed to the boiler. A float type meets the code and then the probe type could be 24V. Main thing is safety and a redundant lwco is a good idea. No control is maintenance free so follow the cleaning interval for the probe type and flushing of the float type.
0
Comments
-
Low Water Cutoff - Probe Primary - Float Secondary for Steam
We want to install a primary and secondary Low water cutoff for a Peerless 4 section steam boiler. Peerless recommends the Hydolevel CG450 Probe for a primary.
Which would be safer .... to install another CG450 probe in the secondary position or a Float type LWC?
Any opinions?
Thanks,
JK0 -
LWC secondary
Thank you for the info, Dale.
JK0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements