PONPC question
Andy_14
Member Posts: 121
You want the fill valve, expansion tank piped into the bottom of the air separator on the supply side pumping away from the boiler, before the circ. if that makes any sence
When pumping into the boiler you raise the systems pressure and chance popping the reilef valve
When pumping into the boiler you raise the systems pressure and chance popping the reilef valve
0
Comments
-
We just started a big job
using P/S piping . We are piping almost exactly like this diagram shows ( from a post JohnNY started , I hope you don't mind buddy ) . The only difference is the primary circulator will be pumping across the flow of the system , not with the flow .
To the left side of the boiler connections we installed an air separator . This is where I want to pipe in the expansion tank . Will the primary circulator have any effect with regards to the PONPC ?
Thanks in advance , Ron .0 -
Possibly...
All pumps SHOULD pump away from the PONPC. As it pertains to the boiler pump, it would be pumping TOWARD the PONPC, which means it would present its pressure differential as a drop in pressure through the boiler. Not a good idea on high pressure drop/high temperature applications.
Provided that you are not dealing with the need for a high residual operating pressure due to elevation, if it were me, I'd put the boiler pump on the boiler return or inlet, pumping AWAY from the PONPC, but towards the boiler.
I don't know if you remember the "conversation" we had a few weeks ago on this Ron, and the only thing I think we determined is that there really is no industry wide concensus on which pump is considered the "primary" pump, but my suggestion was that the pump, or pumps pumping away from the air seperator and the PONPC would be considered the primary pump, or pumps in your case, and then any heat sources would be a secondary heat INPUT connections.
Just my $0.02 worth on the subject.
ME0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements