furnace orifice size
Bob Harper
Member Posts: 1,091
Per NFPA 54, a #53 D.M.S. drill gauge orifice at 11 inches water column will flow 28,769 BTUs per hour at sea level.
Andersen-Forrester sells gauging drills with charts.
HTH
Andersen-Forrester sells gauging drills with charts.
HTH
0
Comments
-
furnace orifice size
I'm working on a furnace that was set up originally for natural gas, was switched to lp gas then back to natural gas. there's a little green sticker someone put on the gas valve indicating the valve regulator is for propane so I'm going to change that. but how do I know the orofices are the correct ones. the manufacturer is "intercity products and I don't know how to get in touch with them. there are 6 tubes that the gas shoots down and burns in the heat exchanger. I took out one of those little nozzle things and it has the number 53 on it. how do I know if that size is for propane or natural gas?0 -
GO here...
http://www.icpusa.com/
Give them the model number and they will tell you what the correct orifice size is.
ME0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements