Luxaire gas orifice change

If your furnace is over-fired it also could be very dangerous. Did you do a combustion test? What is your plenum temperature?? I would probably lower gas pressure but not without a combustion analyzer. That is like lighting a stick of dynamite blindfolded.

Comments

  • Riverrat35
    Riverrat35 Member Posts: 16
    Luxaire gas orifice change

    I have a Luxaire gas furnace 80% model GM8S130D20UH11B.The furnace shuts down fter a few minutes on over temperature.The btu value is very high , 1167 btu's per scf dry.The installed burner orifice is #45.Can I cut down the heat output with smaller orifices,or cut gas pressure to burner.Luxaire says to change orifices but won't tell me what size because I'm not a certified installer with them.I have my own HVACR Business (20 years).My theory is this unit was simply oversized
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    Had to read that twice

    Where in the blazes are they pumping gas with 1167btu/Ft?

    First thing I'd look at is the duct system. You mentioned oversizing and you can look at that two ways with F/A. The furnace can be oversized for the house and still not trip the high limit. BUT! if it's oversized for the duct system, now you have a problem. As long as you're getting enough airflow to keep the thing operating at required temps all you'll have is short cycling. I'd suspect that you'd have to reduce the input so far that it wouldn't be practical if the duct system is undersized. You can only cut your primary air so much to compensate for the reduced fuel supply.

    Before you adjust fuel pressure or volume, see what the CFM of the system is. From the model number it looks like the furnace has a 5T blower which means that even in heating mode you should still be getting 1,400-1,600CFM.


    You could try the gas pressure route but check your flue temp and gases with an analyzer to see if all parameters remain as they should.
  • Riverrat35
    Riverrat35 Member Posts: 16


    This furnace is in Pa lots of gas wells in area.customer had gas analized professionally.Has methane ethane and a host of other anes (lol)in it.I havent seen system yet.Im guessing duct system is not getting the heat out of the furnace as you sugested
  • flange
    flange Member Posts: 153


    you should be able to get this system in line using an analyzer. setting the gas to 3.5 isn't the answer. this is a starting point only and needs to be checked. even luxaire will tell you that if you ask. they assume that you already did that.
  • Riverrat35
    Riverrat35 Member Posts: 16


    Thanks for the help. I think I,ll leave this one to someone else.this has the potential to become a ten year headache.
  • Techman
    Techman Member Posts: 2,144
    LuxAire

    Or you could become the hero!!!!