low loss header
Couderay
Member Posts: 314
Was wanting to build a low loss header for my boiler,does the header need internal baffles for it to work properly.
0
Comments
-
It depends...
Sometimes it makes for good marketing. ;-)0 -
LLH
I tend to think no. Though if you have an automatic air vent in the top I could see a baffle helping air removal. Viessmann offsets their ports instead of a baffle. Caleffi uses a baffle instead of offsetting their ports. If you are zone pumping, I would offset the ports by one pipe diameter. If you are using zone valves, it makes less difference.
-Andrew0 -
From an engineering standpoint
You are looking at a "direct contact" heat exchanger. They work best if you do something to create a mixing environment. While their are a variety of solutions... If you want a short Low Loss Header you can either use baffles or offset nozzles to create a mixing environment.
So pick your poisen as it best matches your situation.
Best of luck.
One question to consider - can you really build one cheaper than you can buy one - when you consider time and materials? The Viesmann one comes with all the ports, a temperature sensor port, vent port, drain port, and you can even get an insulation package.
Perry0 -
Offset or
some sort of screen. I like the Caleffi approch with a perforated metal screen, it creates a good mixing mechanism as well as aiding in air seperation. Plus some ability to catch and drop dirt or debris out of the flow.
I also like the nice preformed insulation jacket for the Caleffi Hydro Seperators, and it is now available with sweat unions.
I'd think ports directly across from one another, without a baffle, would be least desireable.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements