heating unit blower won't shut off

joann_2
joann_2 Member Posts: 2
Hello,

I live in a new condo development with garden style condos. Heat is propane gas. The heating unit in my condo is set at a 73 degrees. The blower has been constantly on for the past 24 hours, blowing air, but not hot air. I finally turned the heat off. Are we out of propane or is this some kind of energy saving thing? Should I call someone to look at the unit?

I appreciate the guidance. Joann

Comments

  • tom_49
    tom_49 Member Posts: 267


    Joann,

    Is the fan switch on the thermostat set for auto or on? Make sure its on "auto".

    Have you changed the filter lately?

    Tom
  • Timco
    Timco Member Posts: 3,040


    Call someone. It is likely the safety circuit has a bad sensor somewhere in the loop. This causes the blower to just blow, with no heat. Could be a rollout sensor (some have a little reset button in the middle) and could be a high-limit sensor, which fails sometimes due to a dirty air filter.

    Tim
    Just a guy running some pipes.
  • tim smith
    tim smith Member Posts: 2,841
    fan stuck on.

    I would say probably 80% of the service calls we have w/ a problem like you state is a plugged air filter and furnace has tripped the high limit air temp to protect furnace. It may be a manual reset or a failed auto reset type. Good luck. Tim
  • Empire_2
    Empire_2 Member Posts: 2,340
    Joann

    It''s always a good idea to have four Heating and A/C checked annually for safety and proper performance.