Converting to hot water.
virtualplumber
Member Posts: 35
I have a customer with two third floor steam radiators that bang like crazy. They are fed with a 3/4 " copper line and have an 1-1/2" copper return. I have shut them off at the radiator valves and the banging has stopped. So in order to avoid tearing a very nice stairwell all to pieces and repiping the thing in iron. I thought about converting it to hot water, and adding a wireless thermostat for those two radiators only. Do you think this is a good idea? Any input would be greatly appreciated.
0
Comments
-
Converting to hot water.
I have a customer with two third floor steam radiators that bang like crazy. They are fed with a 3/4 " copper line and have an 1-1/2" copper return. I have shut them off at the radiator valves and the banging has stopped. So in order to avoid tearing a very nice stairwell all the pieces and repiping the thing in iron. I thought about converting it to hot water, and adding a wireless thermostat for those two radiators only. Do you think this is a good idea? Any input would be greatly appreciated.0 -
Are these 2-pipe radiators?
If so, do they have traps on the return connections?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
2 pipe
Yes they are two pipe and they have traps
0 -
You probably either
have bad trap elements or inadequate air venting on the dry return. If these are OK, try replacing the traps with ones that have larger throughputs like the Barnes & Jones #122.
This should be easily fixable without doing such a risky conversion.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements