boiler service

tom_11
tom_11 Member Posts: 58
On a Weil McLain 68 steam oil fired boiler what do you use to seal the mounting plate to the boiler i want to vacuum the chamber out. thank you Tom

Comments



  • Best way to clear out the chamber is with a flexible nozzle through the burner flange. When your done just replace the flange gasket and re-mount the burner. Dont forget to check the Z dimention while you have the burner out.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • brucewo1b
    brucewo1b Member Posts: 638
    Tom

    As Norm said you can clean through the burner mounting hole, however many of this units by now have flue gas seepage by the chamber mounting plate and I now use 3/8 stove rope around the plate glued on with RTV Silicone and it makes a better seal than the gastket material that is sent with the chamber kits. I was told by Al from Portland I think that a bit of anti-seeze on the boiler before putting back together will keep the gasket from sticking in the future.