Thanks Steamhead and Gorton

Bob C_2
Bob C_2 Member Posts: 8
Let me start off by saying "I wish I did this last year".

About a year ago, I asked Steamhead for the correct vents for my single pipe steam system. The 2 1/2 inch mains go off in 2 directions with lengths of 15 and 39 feet. The returns are 1 1/4 inch pipe with vents located at the end of the returns before it drops. I replaced all of my radiator vents last year with VariValves and ended up putting them on the mains. I put 1 vent on the short main and 3 on the long main.(On a side note, I called VariValve and they said their 1/8 vents can be used on the mains. They market the valves as radiator and main vents.) My system did heat faster last year but I was still was not satisfied.

If you wonder how I came up with 1 VariValve vent on the short main and 3 on the long main, I'll tell you. Highly scientific. I'll put 1 vent on the short main and since the long main is 2.6 time larger, I'll round up to 3 and add 3 vents. LOL

I was reading some posts last week about venting and decided to finally buy the vents that SteamHead recommended. A Gorton #1 on the short main and a Gorton #2 on the long main.

I changed the vents this weekend. Looking at a Gorton #2 compared to 3 VariValves made me laugh. After installing the vents, I turned up the heat and measured how fast the steam reached the ends of the mains. I used the highly scientific method of holding my hand on the pipe and looking at my watch.

I held the pipe at the first elbow above the boiler until it got hot then I went to the end of the short main. It took 3 minutes 15 seconds for the end of the main to get hot. I walked over to the long main and it took an extra 45 seconds for it to get hot. So, both mains get hot after 4 minutes. This is A LOT faster than before.

Is 4 minutes good?

Now that I have my mains balanced better, I can play with the radiator vents. Since the mains where not balanced properly, I needed to compensate with the radiator vents. This is getting addicting.

Thanks Again,
Bob

I really like the VariVents when used on the radiators, just not the mains.

Comments

  • Bob_43
    Bob_43 Member Posts: 16
    Steamhead

    Steamhead,

    I'm still getting some hissing during heating and a vacume at end of cycle from the two radiators at the end of the longest main with the gorton #2. Should I add a Gorton #1 or another #2 on this main to help with the hissing and vacume? If you read my post above, the main is still about 1 min behind the short main when heating.

    Thanks,
    Bob
  • Apparently

    that long main wants more venting. This isn't the first time I've seen this happen, but you have to start somewhere and Gerry & Steve's venting measurements are the best I've ever seen.

    Try adding a Gorton #1 teed on the riser with the Gorton #2 on that long main.

    Regarding the vacuum: are ALL your steam pipes insulated?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Bob_43
    Bob_43 Member Posts: 16


    Yes, All insulated. I will add a Gorton #1 and see what happens.

    Thanks.