Thanks Steamhead and Gorton
Bob C_2
Member Posts: 8
Let me start off by saying "I wish I did this last year".
About a year ago, I asked Steamhead for the correct vents for my single pipe steam system. The 2 1/2 inch mains go off in 2 directions with lengths of 15 and 39 feet. The returns are 1 1/4 inch pipe with vents located at the end of the returns before it drops. I replaced all of my radiator vents last year with VariValves and ended up putting them on the mains. I put 1 vent on the short main and 3 on the long main.(On a side note, I called VariValve and they said their 1/8 vents can be used on the mains. They market the valves as radiator and main vents.) My system did heat faster last year but I was still was not satisfied.
If you wonder how I came up with 1 VariValve vent on the short main and 3 on the long main, I'll tell you. Highly scientific. I'll put 1 vent on the short main and since the long main is 2.6 time larger, I'll round up to 3 and add 3 vents. LOL
I was reading some posts last week about venting and decided to finally buy the vents that SteamHead recommended. A Gorton #1 on the short main and a Gorton #2 on the long main.
I changed the vents this weekend. Looking at a Gorton #2 compared to 3 VariValves made me laugh. After installing the vents, I turned up the heat and measured how fast the steam reached the ends of the mains. I used the highly scientific method of holding my hand on the pipe and looking at my watch.
I held the pipe at the first elbow above the boiler until it got hot then I went to the end of the short main. It took 3 minutes 15 seconds for the end of the main to get hot. I walked over to the long main and it took an extra 45 seconds for it to get hot. So, both mains get hot after 4 minutes. This is A LOT faster than before.
Is 4 minutes good?
Now that I have my mains balanced better, I can play with the radiator vents. Since the mains where not balanced properly, I needed to compensate with the radiator vents. This is getting addicting.
Thanks Again,
Bob
I really like the VariVents when used on the radiators, just not the mains.
About a year ago, I asked Steamhead for the correct vents for my single pipe steam system. The 2 1/2 inch mains go off in 2 directions with lengths of 15 and 39 feet. The returns are 1 1/4 inch pipe with vents located at the end of the returns before it drops. I replaced all of my radiator vents last year with VariValves and ended up putting them on the mains. I put 1 vent on the short main and 3 on the long main.(On a side note, I called VariValve and they said their 1/8 vents can be used on the mains. They market the valves as radiator and main vents.) My system did heat faster last year but I was still was not satisfied.
If you wonder how I came up with 1 VariValve vent on the short main and 3 on the long main, I'll tell you. Highly scientific. I'll put 1 vent on the short main and since the long main is 2.6 time larger, I'll round up to 3 and add 3 vents. LOL
I was reading some posts last week about venting and decided to finally buy the vents that SteamHead recommended. A Gorton #1 on the short main and a Gorton #2 on the long main.
I changed the vents this weekend. Looking at a Gorton #2 compared to 3 VariValves made me laugh. After installing the vents, I turned up the heat and measured how fast the steam reached the ends of the mains. I used the highly scientific method of holding my hand on the pipe and looking at my watch.
I held the pipe at the first elbow above the boiler until it got hot then I went to the end of the short main. It took 3 minutes 15 seconds for the end of the main to get hot. I walked over to the long main and it took an extra 45 seconds for it to get hot. So, both mains get hot after 4 minutes. This is A LOT faster than before.
Is 4 minutes good?
Now that I have my mains balanced better, I can play with the radiator vents. Since the mains where not balanced properly, I needed to compensate with the radiator vents. This is getting addicting.
Thanks Again,
Bob
I really like the VariVents when used on the radiators, just not the mains.
0
Comments
-
Steamhead
Steamhead,
I'm still getting some hissing during heating and a vacume at end of cycle from the two radiators at the end of the longest main with the gorton #2. Should I add a Gorton #1 or another #2 on this main to help with the hissing and vacume? If you read my post above, the main is still about 1 min behind the short main when heating.
Thanks,
Bob0 -
Apparently
that long main wants more venting. This isn't the first time I've seen this happen, but you have to start somewhere and Gerry & Steve's venting measurements are the best I've ever seen.
Try adding a Gorton #1 teed on the riser with the Gorton #2 on that long main.
Regarding the vacuum: are ALL your steam pipes insulated?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Yes, All insulated. I will add a Gorton #1 and see what happens.
Thanks.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements