goldline differential controller
Ericjeeper
Member Posts: 179
I ordered a Wilkins 75 psi PRV today.
0
Comments
-
How do I set it?
On my solar panels.. I had trouble today. I went out and they were not running.. sun was shining bright.I turned the hi limit up and the pump kicked on.. But when the glycol got to my T&P it opened and dumped. the system was at 30 psi.so that means it was over 180 degrees. My storage tank was at 131 degrees. Wheer should the high limit be set? I had the dif set at 12. I am not sure if I have a defective sensor or what. It has been working ok til today. regular old goldline differential controller. Thanks in advance0 -
High limit setting...
is dependent on the storage tanks ability to withstand heat. Typically somewhere around 180 degrees F. Why do you have a T and P relief valve on your solar loop. Should only be a PRV. And trust me, if you started the loop under stagnation conditons with peak solar gain, you were instantly seeing discharge temperaturees in the area of 350 degrees F. Trust me, I know...
Goldline controls are extremely suceptible to RFI and EMI and it CAN scramble their little brains, requiring a cold boot to reset them. Make sure your not running any sensor wires parallel to any high voltage wires, and it is a good idea to use shielded thermostat wire and ground the shields.0 -
what brand or model PRV do I need?
My sensor wire is shielded cable yes. and no High voltage near any of it.
I did just add two of the outdoor temp stats that are wireless transmitters into a main station in the house. I will remove those.
I will change out the T&P and get a PRV in there immediately. Tomorrow morning before I leave the house I will turn the pump on manually to make sure I do not dump the pressure again.(won't let it stagnate)Mark, thanks for your input . Eric Enk0 -
An Ohm meterwill test the sensors. the last page of the install
> My sensor wire is shielded cable yes. and no High
> voltage near any of it. I did just add two of
> the outdoor temp stats that are wireless
> transmitters into a main station in the house. I
> will remove those. I will change out the T&P
> and get a PRV in there immediately. Tomorrow
> morning before I leave the house I will turn the
> pump on manually to make sure I do not dump the
> pressure again.(won't let it stagnate)Mark,
> thanks for your input . Eric Enk
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
An Ohm meterwill test the sensors. the last page of the install
> My sensor wire is shielded cable yes. and no High
> voltage near any of it. I did just add two of
> the outdoor temp stats that are wireless
> transmitters into a main station in the house. I
> will remove those. I will change out the T&P
> and get a PRV in there immediately. Tomorrow
> morning before I leave the house I will turn the
> pump on manually to make sure I do not dump the
> pressure again.(won't let it stagnate)Mark,
> thanks for your input . Eric Enk
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
An Ohm meter will test the sensors.
the instruction sheet has the readings at various temperatures. Be sure the switch is in the auto position on the control. It's easy to catch the off position by mistake. Especially with the cover on.
A simple way to test the control is wire both sensors at the control. Heat the collector sensor with a match or lighter, SLOWLY, and you will hear it click on and the output light will also turn on.
Be sure the solar panel sensor is in contact with the panel or piping near the top and has insulation around it.
If a sensor fails I believe the control fails to the always on?
hot rod0 -
PRV recommendation
75 psi is probably what you want, the weak link is the expansion tank. Stagnation WILL exceed 75 psi, so you still can have an issue in summer.There was an error rendering this rich post.
0 -
Caleffi solar components
their air vents and PRV are listed at 320 and 390F if you plan on high temperature operation.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I have noticed lately
The third light for device number 2 stays lit all the time. I do not even have a wire to those screws. is there something wrong with the controller?
The middle light comes on when the pump runs and goes off when it is off, like it is supposed to/.
To my original question. what should the high limit dial be set to? How does it work? as an over ride? I do not understand its function. Thanks in advance0 -
The third light...
Goes to a drain down valve or other means of freeze protection.
Set the high limit (storage tank temp) to 180 degrees F provided that all components connected to and immersed within the tank can withstand that high a temperature.
If you go with a pressure only relief valve, the thermal capcity needs to match the thermal output capacity of the solar array. Assume 150 btu's per square foot per hour and you should be covered.
ME0 -
Goldline controller
Here is a link to the GoldLine controllers:
http://www.goldlinecontrols.com/Solar.aspx
If your controller is the GL-30, the third LED is for "Freeze recirculation" That option can be disabled. Check the I/O document.
Larry C0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements