furnace faults out after reaching set temp on thermostat main bg

don_182
don_182 Member Posts: 69
like you are riding high on your temp rise and the limit is taking it out.

Lack of airflow.

Comments

  • bernie_5
    bernie_5 Member Posts: 2
    furnace fault

    furnace faults out after reaching set temp on thermostat.main blower&inducerblower stay running.manual says typically caused by gas valve that leaks through or is slow to close.put new valve on still same problem. help,THANKS IN ADVANCE..
  • Charles G.
    Charles G. Member Posts: 113
    Furnace fault

    Some counterflow furnaces were doing this @ end of cycle--residual heat would trip limit @ blower compartment. Age of unit? Possibly need to reset fan off time/temp.