pri / sec question

Timco
Timco Member Posts: 3,040
Does the pri loop need any flow control? 30' or so of 11/4 pipe with a 007 moving it. 162,000 BTU atmos CI boiler.

Thanks,

Tim
Just a guy running some pipes.

Comments

  • Timco
    Timco Member Posts: 3,040


    Second....how many BTU's typical for a 60 gal indirect?

    Thanks,

    Tim
    Just a guy running some pipes.
  • Floyd
    Floyd Member Posts: 429
    I install one...

    use B&G Checktrol flanges for the pump, so they are built right in.
    As for the indirect, you can find charts that will give recovery rates for different flows and boiler BTU's, like this for the WM tanks.

    http://www.weil-mclain.com/netdocs/ratingsplus.htm#RATINGS

    Floyd
  • Timco
    Timco Member Posts: 3,040


    Is there a GPM we are looking for?

    T
    Just a guy running some pipes.
  • Floyd
    Floyd Member Posts: 429
    That's up to you...

    within reason and pipe sizing.... as that graph shows... more flow, more hot water, more btu's more flow needed. One thing to watch is that some indirects run very high heads and you need to take that into account when sizing the pump and piping.

    Floyd