water hammer

Jorge
Member Posts: 26
I have two zone valves one for first floor baseboard and one for 2ed floor baseboard. when a zone turns off I can here a bump soud coming from the baceboard. Boath zones can be on or only one zone on same sound when valves turn off.
0
Comments
-
Water hammer
I have a water hammer noise in my baseboard heat every time the zone valve turns off. They are honeywell zone valves and they are mounted on the feed side of the boiler. Boiler temp is 180 and psi is 20.0 -
Bada-Boom ina pipes
You mentioned only one zone valve, what about the other zones? How many zones in total and what are they for? Pics?0 -
Pipe Banging
Normally this can be resolved by removing one of the return springs on each valve. The problem normally happens when two zones are calling and one satisfies and closes. The valve closes too fast and creates this banging noise. By removing one return spring on each valve it will close slower and not try to bounce back open while closing.0 -
Thank You Ron I just tried it and it worked0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements