What Temp for Hydro Air

Is this a house or a poorly insulated airport hanger? Do you have a copy of the heatloss performed on this structure? If not you should get one...

Rick

Comments

  • Augie
    Augie Member Posts: 4
    Hydro Air Temp

    I have a new house with a Hydro air system with 2 zones with there own air handlers(Caarrier) feed by 1 Larrs 225 btu minithrem boiler with a set point @ 180 degrees

    What would think the temperature of the heated air at the registers should be ?

    My system reads 140 + degrees at the closest register to the coil, and I am thinking about lowering it and or putting an outdoor reset in.

    Augie
  • Ray M
    Ray M Member Posts: 94
    wow

    You must have a large house for such a big boiler! Only two air handlers? The temperture depends on the manufactures coil. They have a chart showing BTU@EWT@GPM.

    Ray M
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    Ray

    Probably not that big! More than likely the conversation went like this, Billy Bob :"I seen a house like this once and it had a 175k BTU boiler" Jethro: "In that case we better use 225K because you never know,you know?"

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • jp_2
    jp_2 Member Posts: 1,935
    so,

    you can tell if a boiler is properly sized just by knowng the size of the boiler?
  • Ray M
    Ray M Member Posts: 94


    I do a heat loss they do a walk through. 5 ton's here 125k coil.It will work fine.

    Ray M
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    No

    I can't. But If Augie wants to provide prints,we can do a heat loss and if the 225K boiler in his house is not oversized by 20%.I will donate $100 to Dan's charity of choice. We on?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Ray M
    Ray M Member Posts: 94


    I have installed smaller boilers in 8k square foot home's with 6 air handlers. There is a thing called diversity.

    Hope this helps
    Ray M
  • Ted_9
    Ted_9 Member Posts: 1,718
    Devil's Advocate

    I googled this. The output is about 185,000 btu's. I also beleive the boiler is over sized though. Just wanted to throw that info out there.

    http://www.laars.com/productdetail.htm?ProductLineID=JV&PicFile=JV

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jp_2
    jp_2 Member Posts: 1,935
    laars web site

    as ted said, the 225 has an output of 186.

    as you say, if the 225 is 20% oversized, that would be a heatload of 155,000btu.

    the next smaller boiler is at 133,000(output) so the installer would have to oversize or undersize by 22,000 btu. how many installers typically undersize?

    from nearly all the recent posts, boiler problem posts seem to be grossly oversized, I was just giving you a hard time, no facts give you no answers, onlly questions.

    maybe its a huge house, 5 kids, tons of big window, northern minnesota, outdoor year round 500gal hot tub? do we know?
  • jp_2
    jp_2 Member Posts: 1,935
    augie,

    my question would be, whats the register temps farest from the coil?

    that will be the determining factor. if its too low, of course, that area will be uncomfortable.

    so give us some details:

    house sq ft.

    where are the two air handlers, 1st floor 2nd floor

    normal winter lows

    other 'stuff' connected to the boiler