One-pipe primary-secondary systems

FrankieJ
Member Posts: 2
Is there a rule of thumb for the distance of piping between pairs of closely spaced tees? I am attempting my first P-S piping system. I am currently in the design stages.
0
Comments
-
As closely as you can
Often a close nipple will do. Taco has a fitting series where they enter and leave in one fitting with a divider between. Yes, that close.
Having 5-7 diameters at least of straight pipe upstream and downstream cannot hurt either.
The idea is that the space between the tees should have no appreciable pressure drop; take away any excuse for flow in that circuit to want to leave of it's own accord. Flow in one circuit should never affect the flow in the other.
Sometimes if the tees have to be a distance apart for some reason, (obstruction for example) increasing the tee assembly one size for that installation is a good idea.0 -
Should the distance between the closely spaced tees of circuit A and circuit B be as close as possible also?0 -
Yes,
For the very same reason, that one circuit not affect the other.
Here is another way to look at it. Suppose each pair of tees in each circuit had a ball valve between them, a tee on each side of even a full port ball valve. There is more pressure drop between them then a short nipple. Some flow, -not much, but some- will be induced to take a side-trip just because it is lazy. Even a trickle, until the pressure drops of the straight path and the branch path become equal.
Now start closing the valve and what happens? Flow will be forced from one circuit to the other, affecting flow in it even more.
Make sense? Works both ways, too.
Cheers!
Brad0 -
Closely space tees
The rule of thumb is no wider then 5 times the pipe diameter for the tee spacing.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements