pri/sec piping & bypass?
Timco
Member Posts: 3,040
Is there a specific rule of thumb for applying pri / sec piping? If this method is used, is a boiler bypass needed?
Thanks again,
Tim
Thanks again,
Tim
Just a guy running some pipes.
0
Comments
-
Tim
Could you be more specific as to type of boiler, (e.g.: cast iron, mod-con, copper tube, etc.) type of system (e.g.: converted gravity, fin-tube, radiant floors, etc.)
Just want to be sure what the application is and why you are asking.
As a general answer, primary-secondary in effect works as a bypass by maintaining the boiler temperature independently of the distribution temperature. How that is done differs of course.0 -
Thanks a lot for the reply....I am replacing a snow man with a cast iron atmospheric boiler, 162,000 BTUH. The old system has two 2" loops. Figured I would move these seperate wit 15-58's rather than as one zone with a 2600 series. Now it has a big 'ol B&G and the water moves too fast. Takes forever to heat up. Heatloss is just shy of 160,000. Would pri / sec be better than a fixed flow control on a bypass? No reset for now....I quoted and they opted for later.
Thanks again,
TimJust a guy running some pipes.0 -
Forgot to mention this system has many rads....CI. If dist temp does not need to be independant of the boiler temp, as with slab heat, then a typical bypass is the ticket?
tJust a guy running some pipes.0 -
Tim, I prefer P-S
and the secondary circ should be sized to the EDR rather than the heat loss. How much EDR is there?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I have that number somewhere....Will need to find it. I got the total EDR for each rad, but am not sure what rads are on what loop. Two loops. If I am using 15-58's, shouldn't I be able to dial them in?
Thanks again,
TJust a guy running some pipes.0 -
Probably
but I bet you find you can run both loops with just one 15-58 or similar circ. There's only so much radiation you can serve with 2-inch pipe.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I was figuring the cost of 2 15-58's was less than one 2664. House is fairly large...runs up 3 storis then out from there as best as I can tell. I tend to play safe & oversize...that's the beauty of the 3-speed selection.
TJust a guy running some pipes.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements