WeilMcLain sgo4

We just recently installed this boiler, it is not new but only bout 3 yrs old. It has been operating for a month without a hickup, suddenly Wed afternoon it kicked off on safety. First thought was inline filter so changed it. It takes several attempts to get the controller to reset, then it runs fine till thermostat is satisfied and shuts off, then when heat is called for again it goes off on safety. Really puzzled, fuel is fine, everything works fine for the one cycle then zap.
Any hints greatly appreciated.
DAN Havent talked to you in many many years hope all is well with the family. You probably dont remember but you designed and helped me with the old Burnham steam critter I just replaced. Am in Netcong NJ, we met years ago in a steam seminar at the Garden State Expo Center near Boundbrook NJ.
Thanks in Advance
Custom Carpentry by Jack
Jack M
973-945-6686 Cell

Comments

  • Ed Wallace_4
    Ed Wallace_4 Member Posts: 1
    boiler

    sounds like it might be the cad cell relay have your oil company check it
  • Jack Mazzuchelli
    Jack Mazzuchelli Member Posts: 3


    Ed; Thanks for the reply would call you except for a small detail LOL LOL you didnt leave a phone number on my voicemail, either email or call me with it and I will call, thanks again
    Jack