sp-80 Tempstar Furnace
Chipper
Member Posts: 2
Hello,
I have a SP-80 Tempstar natural gas forced air furnace that is 11 years old recently i had the blower removed and cleaned the person who cleaned it said there was 2 oil ports
for the motor and ask me for some 3 in 1 oil he put some in each port and put the caps back on, anyway he re- installed
the blower and it works great, i had found the owners manual for the Furnance and looked under maintance and it said to use sae 10w30 motor oil only and to not use 3 in 1 oil because it may damage the motor is this correct?in what way could the 3 in 1 oil damage the motor?and should i be worried about this?
any advice apperciated
Chip
I have a SP-80 Tempstar natural gas forced air furnace that is 11 years old recently i had the blower removed and cleaned the person who cleaned it said there was 2 oil ports
for the motor and ask me for some 3 in 1 oil he put some in each port and put the caps back on, anyway he re- installed
the blower and it works great, i had found the owners manual for the Furnance and looked under maintance and it said to use sae 10w30 motor oil only and to not use 3 in 1 oil because it may damage the motor is this correct?in what way could the 3 in 1 oil damage the motor?and should i be worried about this?
any advice apperciated
Chip
0
Comments
-
3 in 1
It is too light and it will clean out the bearings. Not to worry.It will run out quickly.Wait a while and reoil it in a few weeks of running time. I like to use a non detergent oil on sleeve bearings. The build up of grease is a good thing..0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements