zone valve versus flo check valve...
Jim_95
Member Posts: 11
Is it possiple not to get enough BTU's through a zone valve due to rduced port zize?
Which option is best for a Gas boiler, 3 zone installation with domestic hot water heater.
1. zone valve per circulator with taco 4-zone with priority controller.
2. one circulator, zone valves for each zone with taco 4-zone with priority controller.
3. flow check valve per circulator (can use taco's circulator with IFC option?).
Option 3 Eliminates need for zone valves and zone valve controller. How do you setup DHW priority without a controller?0 -
ronyd
I would use the Taco ZVC403 and wire it as in page 31 http://www.taco-hvac.com/uploads/FileLibrary/100-9.0.pdf
You want the DHW tank on its own circulator and the Taco control realy makes wiring and trouble shooting the zone valves a snap.0 -
I vote for option 2.0 -
Carol,
why option 2? Is it wise to have a single point of failure? I was thinking if a circulator or valve fails, still have heat from other zones.
your thoughts are appreciated...0 -
ronyd
with zone valves if the circ fails no heat at all. but if a zone valve fails it can be manually opened and closed for heat to that zone, if a circ zone fails no heat to that zone at all. Just depends on preferance although power consumption is less with zone valves.0 -
my other thought was, if I have shutoffs on each side of the circulators, I can service the zone myself. Just go to the local HomeDepot, get a taco circulator off the shelf, and replace it. I'm afraid with one circulator, I'm down until I can get a plumber and/or plumbing supply to purchase. Double Home depot carries large circulators.
But point being, as long as I can open the zone valve manually, I got temporary heat.
My question still is, a circulator for each zone valve or one circulator serving all zone valves?
ronyd
either one circ with zone valves or a circ with checks for each. Also I would check into Grundfos usp 15-58 3 speed circs as you are going to dealing with multiple head losses and this will better cover all your bases.0 -
Bruce,
I contractor is specing with one circulator/multiple zone valves, the other specing multiple circulators/multiple zone valves, both using the taco zone controller. Mulitiple circulator approach just overkill, or they just don;t want to determine the proper sizing of using one circulator?
Can;t figure these contractors out. Seems like they want to do things the only way they know, usually word of mouth from other contractors on what they do.0 -
ronyd
Well one circ multiple zones is fine as long as the cic is sized for the highest head zone. I don't understand why one would want both zone valves with cirs on one circut, unless they don't like check valves, now I never put more than three zone valves to a circ but you have threee heat zones and one DHW zone that should be on its own circ.0 -
Are zone valves better than using flo check valves?0 -
I think
that the cost oof zone valves are about the same as circs so either or would be the case0 -
Zone and flo checks
In some DHW priority systems, it is possible for the stats to do a heat call and open the zone valves when the DHW circulator is running in priority. Those systems require check valves on both the DHW and heating loops.0 -
Bruce,
Not to beat a horse over the head on this issue. But, in priniciple why use zone valves over flo check valves or vice versa?0 -
In my experience. zone valves for the heating zones on a common circulator. It's a simple install, and if the circulator goes bad there is usually enough gravity heat through the open zone valves to keep the pipes from freezing. If a zone valve goes bad it can be manually opened until it's repaired.
The domestic water heater, I assume you mean an indirect heater running off the boiler, should have it's own circulator with flow check to assure proper flow and plenty of hot water production.
I have seen a lot of jobs with the circulator/flow check option. It seems that plumbers especially like to go that route. I think it is over kill, unless you have a huge house with need for a lot of flow.0