steam question

filled with water. It may be hidden in a wall or ceiling. Do whatever you must to unearth it.

Another possibility is that the rad shutoff valve has broken, and part of the valve is blocking the steam flow.

What is the EDR of the rad in question? If the horizontal runout is 25 feet and only 1 inch, it might be too small. Those long runouts require either larger pipe sizes or riser drips to the wet return to work well.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • j a
    j a Member Posts: 11
    STEAM QUESTION

    RECENTLY INSTALLED A BURNHAN PIN3 STEAM BOILER FOR A 2ND FLOOR APARTMENT. NEAR BOILER PIPING WAS DONE PER BURNHAM SPECS. BOILER RUNS FINE. I SIZED THE BOILER BY MEASURING THE TOTAL EDR AND BOILER MY BE JUST SLIGHTY UNDERSIZED.I RELOCATED THE MAIN VENT TO CORRECT POSITION AND REPLACED IT. I ALSO REPLACED ALL RADIATOR VENTS WITH VENT RITE #1 VENTS.MY PROBLEM IS THIS THE KIT RADIATOR WAS A ADD ON YEARS BACK AND I CANT GET STEAM TO IT EVEN AFTER TAKING THE VENT OFF..BACK TO THE BASEMENT I GO AND LOOK AT THE PIPING THIS RADIATORS TAKE OFF COMES OFF THE VERTICAL RISING OUT OF THE HEADER,IS THIS WRONG AND WHAT SHOUD I DO TO CORRECT IT.....THANKS FOR ANY AND ALL HELP J A
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Check the pitch of the piping

    my guess is there's a low point in the piping between the main and the rad, where water can collect and block the steam.

    If this isn't the problem, check the pipe size against that of the other runouts. It might be too small.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • j a
    j a Member Posts: 11
    STEAM QUESTION RE

    PITCH IS GOOD, PIPE SIZE IS 1 INCH. HORIZ RUN APPROX 25 FT THEN UP TO 2ND FLOOR HORIZ RUN GETS HOT THEN STOPS AT VERTICAL. WITH VENT OFF AIR IS PULSING OUT TAPPING..