vitodens: bypass needed?
Mike T., Swampeast MO
Member Posts: 6,928
You caught me.
I can't find in the literature supplied with my Vito right now, but it's at least <I>implied</I> over and over by the minimum flow rate.
I have some Vito literature from the UK here somewhere and am nearly positive that it actually refers to TRVs and differential pressure bypass. The only place I've seen TRVs mentioned in my literature is in the <I>user</I> manual where it's something like "if too hot turn down the TRVs."
Manual definitely does not mention the built-in bypass as it's not intended to be used for the emitters--only for the boiler itself.
I can't find in the literature supplied with my Vito right now, but it's at least <I>implied</I> over and over by the minimum flow rate.
I have some Vito literature from the UK here somewhere and am nearly positive that it actually refers to TRVs and differential pressure bypass. The only place I've seen TRVs mentioned in my literature is in the <I>user</I> manual where it's something like "if too hot turn down the TRVs."
Manual definitely does not mention the built-in bypass as it's not intended to be used for the emitters--only for the boiler itself.
0
Comments
-
pressure bypass on vitodens: is it necessary?
ok, so i'm installing a vitodens 200 6-24 piped in series to a manifold serving panel radiators with TRV's.
my question is, do i need a pressure activated bypass valve in between the supply & return mains? i usually always install them on systems with zone valves or TRV's, but is it even necessary with the vito having its own vari-speed pump & all? does the vito have a transducer that notices valves closing and ramps down accordingly like the grundfos alpha-pro or is it strictly linked to the burner/blower modulation?
i was going to ask my rep today but everyones gone for thanksgivng. (i'm in canada)
thanks!0 -
Viessmann
Viessmann says yes, though I've seen them work just fine without.
-Andrew0 -
Vitodens literature says that you should use a differential pressure bypass valve with a fully TRVd system.
There's a small built-in differential pressure bypass, but was told that it's only there to handle the transition between space heating and DHW production.
I can verify that it's there--I've heard it.
0 -
where would i find this info?
i've read through all the manuals several times and found no mention of a bypass (even the built in one) where did you read this?0 -
dP
We asked Viessmann's engineers in Waterloo last year, and they said a separate dP bypass must be used.
It is mentioned in the Troubleshooting Guide in items 4 and 6. TRV's aren't exactly zone valves, but I suspect to maintain proper flow through the boiler, a dP valve will be recommended if not required.
-Andrew0 -
ok, I think that answers my question
I also found on viessmanns UK site something along those lines as well: UK installation guide "The boiler incorporates an internal bypass, however one radiator should be permanently open..."
thanks all for the replies!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements