Sizing pump for Indirect
Rob_34
Member Posts: 21
On a previous post with pictures of a Weil McLain install there were comments on the size of the circulator for the indirect. I was going to install a Bradford White Power Core 80 gallon and wanted to know what size cirulator I would need. I always thought that head pressures were low in the indirects.
Rob
Rob
0
Comments
-
Head loss
That particular indirect, with the fittings in the top of the tank, has extremely high head loss. I would recommend a 26-99 on that tank to maximize performance. The coil is long and small diameter.
-Andrew0 -
All indirects are not created equal...
as was stated this indirect needs a high head pump and may not even work with some Mod/Con unit combinations, because you simply cannot drive enough water through that coil....
Even with basic boilers, flow is directly linked to the amount of hot water that can be made by the indirect.....
Floyd0 -
BW has redesigned their
indirects. I'm not sure what vintage you have, but the new ones are 1-1/4" coils. Also with the updated CombiCor. Large diameter enamaled steel coils.
The older ones had a 5/8" diameter looooong coil. Quite a bit of pressure drop, although I have flowed them with a 15-42. Just takes a while to recover
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements