indoor reset
J.C.A._3
J.C.A._3 Member Posts: 2,980
You can try thr Buderus site and look for instructions for the GB142 boiler. They ship all of them with the BC-10 controller for indoor reset. They are now also sending the AM-10 for outdoor reset, and say to use one or the other. They will not work together
Hope that helps. Chris
  • Ike Gatlin_2
    Ike Gatlin_2 Member Posts: 4
    Indoor reset
    Can any of you point me int he right direction to learn some of the Euros practices based on the concept of indoor temperature reset?
    You ... who what why etc...
    Ike Gatlin
  • Joe@buderus_2
    Joe@buderus_2 Member Posts: 302
    Indoor reset
    With indoor reset, the system water temperature is based on the Room sensor set point and the actual room temperature. A change in the room sensor set point will have an immediate change in the system water temperature. Constant circulation is used and the water is adjusted slightly to meet the demand (like cruise control in your car.) With outdoor reset the system temperature depends mostly on the outside temperature. Large indoor temperature swings with outdoor reset may result in a longer time to reach the indoor set point. European systems usually don't have as many zones and rely on thermostatic heads for individual room control. Both type of resets work in a properly designed, installed system.
  • Paul Rohrs_5
    Paul Rohrs_5 Member Posts: 134
    TN4
    Ike,
    Good to see you back in the US. I will note your new email as well.
    Our friends to the north with blue boxes have their latest system TN4 with indoor reset (edit: as well as outdoor-reset). Up to four reset temps (buses) can be employed on one system, but to me the beauty is that even with multiple zones on one bus, the indoor reset will note and calculate the highest rate of heat loss and set the water temp to accomodate that zone. For example, the correct outdoor reset temp for the system for a high-mass radiant infloor might be 110F at design conditions, but maybe one zone in the garage has some doors left open and the rate of heat loss increases. The TN4 system will adjust the outdoor reset temp to accomodate the new indoor reset temp necessary to satisfy that zone. Best of all worlds.
    Regards,
    Paul
  • Perry_2
    Perry_2 Member Posts: 380
    The Vitodens 200
    is capable of using both an outdoor reset temperature curve; and a feedback on indoor temperature with the RS Remote Control module. Essentially the RS Remote Control module tells the Vitoden to adjust which outdoor reset curve it should be on based on actual house temperature (i.e.; bumping the outdoor reset curve up based on very windy conditions that increase heat loss or bumping it down based on solar gain). Better yet, the RS Remote Control allows the Vitodens 200 to figure out which outdoor reset curve it should be operating on if it was not selected right up front.
    The RS Remote Control module also allows nighttime temperature setback for the house - and again modifies which outdoor reset curve the Vitoden 200 is following to accomplish that (The WS Remote control does the same thing for nighttime setback - but does not monitor the actual house temperature.
    Note that the RS Remote Control module may not work for all configurations. In my case I have cast iron baseboard on a monoflow T system. I do not have TRVs and retrofit of them would be difficult for several reasons.
    Installation of my Vitodens 200 will be Tuesday of this week.
    Perry
  • ALH_4
    ALH_4 Member Posts: 1,790
    Shift
    The WS and RS cause a parallel shift in the heating curve. The RS allows the user to shift the normal and setback curves separately. It also allows the user to put the system into automatic operation, or day, or night setback mode. With the Vitodens, only one RS may be used. Unfortunately the best description in the literature that I know of is in the TDM on page 33, which is a very brief description.
    Tekmar has been doing a more sophisticated, multi-zone version of this this with their zone controls for a long time allowing full PID control and zone staggering. This Data Brochure has a pretty good description.
    -Andrew
  • Perry_2
    I agree that the literature doesn't provide a good description
    I got it explained to me by a Mfr rep when I was trying to figure out how a Vitodens could compensate for solar gain and windy conditions. Both of which can alter a house temperature if the heating system is only running on outdoor reset.
    The other thing the RS controller will do - is turn the heating system off if the house is too warm. Something that may be more usefull during spring and fall when the heat load is below the minimum firing rate of the boiler.
    Perry
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Indoor reset comes in a number of forms:
    The simplest is the sort of "automatic" indoor reset you get with old systems using standing iron radiators. When the thermostat calls for heat, the burner fires and the circulator runs. In most weather conditions, the thermostat will be satisifed well before the boiler reaches the temperature of the aquastat. The colder the weather gets, the less the system will cool between cycles and the higher the circulating water temperature.
    With condensing/modulating boilers or more modern systems, indoor reset is much more sophisticated. All I've heard of work on the idea of proportionality and directly communicate with the boiler controller. Instead of just identifying if a thermostat is either "calling" or "not calling", it determines how far the current sensed room temperature is away from the current thermostat setting. The further apart these two values the greater the effect on the reset curve. What the controller is really trying to do is to determine just what temperature is required to keep sensed and desired temperatures exactly equal--this will be the lowest and most efficient possible temperature required to maintain space temperature.
    Often, it's better named "indoor feedback" than "indoor reset". This is the case with the Vitodens remote controls and [probably] most sophisticated reset controls like the Tekmar TN4 system. Here there is still an outdoor temperature sensor establishing a "base" reset curve, but indoor sensors(s) are allowed to modify this curve based on the magnitude of difference between sensed and desired room temperature. If multiple indoor feedback devices are allowed (as with the Tekmar TN4) the process can become EXTREMELY complicated. As mentioned in another message, the controller has to calculate the HIGHEST temperature needed in any of the zones--it will then operate zone valves and/or circulators and/or mixing valves in an attempt to keep the other zones as close as possible to the temperature they require.
    The Buderus GB with RC-10 uses true indoor reset--there is no outdoor temperature sensor. Only one such sensor is allowed. While I believe this is technically the most efficient form of reset, there can be problems in multi-zoned systems. Imbalances between the zones and differing setback schedules among them can cause problems as the area with the RC-10 acts as the true master. 1-2 zones or TRVd systems are likely best suited to this form of control.
  • D107
    D107 Member Posts: 1,911
    Great point about 'automatic' reset
    This is the kind of insight we just can't get anywhere else but the Wall. Never thought of the 'automatic' indoor reset before, that maybe alot of heating is going on at 130, 140 degrees anyhow with old systems. Only those pumps go off when the burner does. With the modern reset systems it seems you'd save more both in cold weather, as circs keep pumping after burner shutoff--with lower supply temps-- and in shoulder seasons when the reset would keep burner off more of the time.
    Interesting to try to quantify in percentage how much additional reset/savings you're getting above and beyond
    the old auto reset when you put in a new indoor (or outdoor) reset. Probably not as much as I thought, though certainly worth it.
    David
  • Ike Gatlin_2
    P Rohrs
    Thanks for the information all.
    Paul,
    you can reach me on my cell anytime. 615-319-3389
    Ike